Hi all, there is a problem on parser of negative temperature for MCF88 devices, I think is a sign issue on parser for MCF-LW12TERWP on negative temperature (and I suppose the same for MCF-LW12TER, MCF-LW12CO2, MCF-LW12VOC).
Instead to have negative temperature, the parsed temperature has high values (over 600°C).
This is an example:
044A716B2769FF89AE88018D726B277BFF85A58801CF736B2781FF85A3880164
04 -> type Temperature/Pressure/Humidity
First measure
4A716B27 -> date/time
69FF - > temperature -> LSB became FF69 -> SIGNED INTEGER if 32 bit is FFFFFF69 -> -151 hundreds of degrees -> -1,51°C
89 -> humidity
AE8801 -> pressure
Second measure
8D726B27 -> date/time
7BFF - > temperature -> LSB became FF7B -> SIGNED INTEGER if 32 bit is FFFFFF7B -> -133 hundreds of degrees -> -1,33°C
85 -> humidity
A58801 -> pressure
Third measure
CF736B27 -> date/time
81FF - > temperature -> LSB became FF81 -> SIGNED INTEGER if 32 bit is FFFFFF81 -> -127 hundreds of degrees -> -1,27°C
85 -> humidity
A38801 -> pressure
64 -> battery
I think there is a wrong handling of 2 bytes signed integer value.
Thanks in advance.